4/29/2006 9:38 AM | |
Posts: 1 Rating: (0) |
Through setting CPU 414-4H MPI toDP,connection two series redundancy system ,this way is right? |
5/14/2006 6:40 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (318) |
Hi Niezhanwen, I think it won't work this way because the MPI-communication couldn't be used in a H-System. [:(] So you have to use CP443-5DX04 Profibus cards with FDL communicationand communicate between the two systems or CP443-1EX11 to communicate between the two H-Systems. That meens two * two CP-cards of one of the before mentioned cards and then a redundant coupling between the four cards. [;)] So it is possible to make different networks, two totally devided networks between the two H-Systems or all 4 CP's on one network [:o] or all CP's on one network, this is then also of the needed redundancy. If this is not enough, you may place 2 CP's after one H-CPU, so that you have in total 8 CP's that are connected over two different networks that might be in a ring, thats real Fault Tolerant.... [:D] I have put a example attached to this question: AttachmentS7H IE-PB Example Project plus Worddocument.zip (209 Downloads) |
Last edited by: Late at: 5/14/2006 6:50 PMSome errors in typing cleared I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|
7/25/2009 12:34 PM | |
Posts: 90 Rating: (1) |
Dear Late, I was looking into your example project and we only found the netPro config. I was looking of which FC or FB to used with two H-STATIONS... Thanks, |