12/22/2011 12:48 PM | |
Joined: 11/21/2007 Last visit: 12/23/2024 Posts: 2325 Rating:
|
Hello samkcr I think you will have to define a seperate connection for each meter as each meter has a different Modbus address. However as per the WinCC Flexible Communication Manual - Vol-2 , ( Section 2.1 Page-250) Pl check out : http://support.automation.siemens.com/WW/view/en/18797249 You can have a Max of 4 connections defined on Modbus Channel. This driver is designed for communication with PLCs on Modbus and although it dows work with other Modbus devices, the no of channels that can be defined is limited to 4 only. Therefore it isnot be possible to have 50 meters as each meter will have to be defined as a seperate seperate connection. Max of 4 meters can therefore be connected. You can consider using a S7-200 ( 224XP ) with Modbus Master or better still use IM151-7/8 with 1SI Modbus Master to act as a gateway. These can collect data from all meters on a Modbus and provide them to the same on a PPI / TCP-IP link to WinCC Flexible. Hope this helps Cheers Navnag |
Last edited by: Navnag at: 12/22/2011 12:49 PMThere is no such thing as the last bug in a program |
|
12/22/2011 2:16 PM | |
Posts: 7 Rating:
|
Hi, when a RS485/ Ethernet converter is in use how do you specify the connection type in WinCC flex? |