6/23/2009 6:48 AM | |
Joined: 10/7/2005 Last visit: 11/7/2024 Posts: 3026 Rating: (1057) |
Hello dilipan_c I had the same problem and as it turns out it only works if you program your PLC to PLC comms as if theywereS7-400 PLC's. What this means is that you use the comms SFB's instead of the FB's in you logic (e.g. SFB14 GET instead of FB14 GET). What "annoyed' me most is the fact thatthe (S7-300 usable) FB14 GET for example contains internally SFB14, SFC20, SFC 51, SFC58 &SCF59 and ALL of theseare meant to be supported by SP3 of PLCSIMV5.4 (i.e. FB14 should work, but it doesn't). I hope this helps |
Last edited by: fritz at: 6/28/2009 12:01 PMCheers |
|
6/23/2009 7:36 AM | |
Posts: 557 Rating: (64) |
hi find the link, hope this will help.. http://www.plc.net.ru/viewtopic.php?t=10730 http://support.automation.siemens.com/WW/view/en/36068796 https://support.automation.siemens.com/WW/llisapi.dll/csfetch/36068796/S7_PLCSIM_V54_SP3.zip regards |
This contribution was helpful to1 thankful Users |
6/23/2009 3:44 PM | |
Posts: 34 Rating: (2) |
tomorrow i will try and let u know regards dilipan
|
7/7/2009 4:28 AM | |
Posts: 34 Rating: (2) |
it works regards dilipan
|