Technical Forum
12/16/2013 1:57 PM | |
Posts: 206 Rating: (22) |
Hello Sarfraz, if you have a new Siwarex U 7MH4950* you can use the GettingStarted example project. http://support.automation.siemens.com/WW/view/en/28391777 In this project all message are already integrated in the WinCCflexible project. If you look to the S7 side of the GettingStarted you see in DB9.DBX107.1 the fore wire break. For the bit to be actual the DR31 has to be read. This is done in the example project in OB31. Thebit for channel one, fore channel two it is respectively DB9.DBX117.1 and DR32. Regards ABenno |