Hello dacastillo; Do you mean how you need to connect the 2 PLCs physically to the single Profibus port on your HMI? The screenshot below shows the "normal" way to setup a Profibus-DP network, using Profibus cable and connectors. Profibus-DP uses a daisy-chain, linear bus configuration, You could c0nnect PLC1, then PLC2, the the HMI; Or PLC1, HMI, PLC2. or... It all depends on the topography of your plant, connect the closest nodes as they present themselves, logically. Termination is generally available directly on the Profibus connectors; the first and the last physical nodes must have the terminator switch at ON. The figure is taken from the Profibus-DP Installation Guidelines, from Profibus.com, a document you should look at for more information on the subject of Profibus networks. https://www.profibus.com/download/profibus-installation-guidelines/ Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 08/04/2020 01:30:56Last edited by: dchartier at: 08/04/2020 01:33:06 |
|
This contribution was helpful to1 thankful Users |
8/4/2020 7:30 AM | |
Joined: 3/30/2020 Last visit: 11/5/2024 Posts: 4926 Rating: (1007) |
Hi. Get a Profibus connector. |
Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to2 thankful Users |
8/4/2020 6:56 PM | |
Joined: 8/9/2017 Last visit: 7/11/2022 Posts: 3 Rating: (0) |
My problem is more how I connect and configure two plcs on one profibus subred and how they communicate with the screen. |
8/4/2020 7:21 PM | |
Joined: 8/9/2017 Last visit: 7/11/2022 Posts: 3 Rating: (0) |
I think my best option is to use a DPDP coupler, but I am locking if there's another way of do this whitout the coupler. |