Ronnie, sorry for the delay. Many problems in this client. This issue has been resolved as follows: In the BT Bacnet Stack Config tab I set the IP of an existing PXC as Foreign Device and everything went back to normal. Very simple. Now I have a new problem with my Modbus (TCP) points. The CSV file is ok al points appears in Desigo , but one of then (Compressor Pressure Sensor) show the value 8 388 610 and in ModScan the value is 8,38. The same of Compressor Panel. I change the resolution on CSV file but don't works. ------------------------------------------------------------------------------------------ |
Last edited by: FERNANDOBR at: 11/10/2021 20:57:52Last edited by: Jen_Moderator at: 11/11/2021 09:52:05New subject after splitting |
|
11/11/2021 7:12 AM | |
Posts: 39 Rating: (9) |
Hi, use script to show the required value. You can do it here: Scripts in Graphics (desigoccecosystem.com) It should be like this: Read("System1.LogicalView:Logical.Site'AS01.B.Ahu10.FanSu;")/1000000
|