Hi, What is the distancelimitation of the wiring from field instrument/sensors to digital/analog IO? Thanks. |
2/25/2013 7:35 AM | |
Joined: 4/22/2010 Last visit: 1/15/2025 Posts: 5697 Rating: (715)
|
Hello, Depends on module used. Guideline is digital unshielded 600M, shielded 1000M Analog max 200M, temp. sensors max 50M You will find this information in: SIMATIC S7-300 S7-300 Automation System Module Data Regards, Marcjan |