Thank yourLate, for your quickly reply, i'll try to use this steps, to write F-CALL. Thanks, Pedja S. |
6/1/2007 8:33 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (318)
|
Hi Pedja, For sending/receiving failsafe data you have to choose in the hardware the right datatypes, for example MS. Then you have a certain amount of data to send and to receive, 16 Booleans and 2 Integers. For every F_SENDDP to every F_RECVDP you have the same amount of data communication. F_RCVDP have to be called as first block into FC13, F_SENDDP have to be called as last block into FC13. Please look in the handbook S7 Distributed Safety - Configuring and Programming You have to call all further failsafe blocks from FC13!! |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|