5/3/2011 6:11 PM | |
Joined: 9/27/2006 Last visit: 11/12/2024 Posts: 12293 Rating: (2691) |
Hello PLC master; Have you looked at the Sentron Modbus TCP sample project, located here: http://support.automation.siemens.com/WW/view/en/40120628 The explanation file states that the Sentron will convert the Double REAL registers for energy metering to "Simatic REAL" 32-bit values befopre transmission over Modbus TCP. By the way, the sample program is designed for CPUs with integrated Ethernet ports (PN CPUs), I hope this is what you are planning to use. Hope this helps, Daniel Chartier |