6/5/2022 9:15 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878) |
Please refer What options does the ET 200S have for temperature compensation when using thermocouples? FAQ which may help you. |
Last edited by: Jen_Moderator at: 06/07/2022 09:56:06Link optimized. |
|
6/5/2022 10:24 AM | |
Joined: 7/3/2006 Last visit: 10/30/2024 Posts: 70 Rating: (0) |
Dear friend Thanks for your reply, I've checked the modules configuration which are so simple, just the thermocouple type (in my case K) and measuring (celsius) but having the same offset for all modules (38 degree), it is very strange to have all this deviation for 15 modules with same offset ??? |
6/8/2022 3:45 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi guys, There is a FAQ that may help: What do you have to watch out for when using thermocouples if the expected value is not displayed?The thing is that thermocouples doesn´t measure the temperature itself. They measure the difference between the tip of the thermocouple and the point where they are connected. Thats the reason why you need a reference temperature. hope this helps, regards, |
FCK WAR! |
|
Follow us on