Posts: 510 Rating: (119) |
If your HMI is WinCC or WinCC Flex, and your HMI is integrated in the Step 7 project, Report System Error will accomplish what you want. Report System Error is configured using the HW Config Editor, Select the CPU and then Menu > Options > Report System Error. It is described in detail in the online help > Configuring messages > Configuring the Report System Errors This link describes getting the system error messages to WinCC: http://support.automation.siemens.com/WW/view/en/22727527 The process for Flexible is even simpler. Bill |
This contribution was helpful to1 thankful Users |
5/22/2014 9:44 AM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question splitted to save the diagnostic messages automatically via the HTML web of the PN CPU Best regards O_Moderator |