6/6/2017 8:37 AM | |
Posts: 7 Rating: (0) |
Hello, I have migrate program from IM 151-8 PN/DP CPU to CPU 1512SP-1 PN, all went well except FB for telegram 352. It was know-how protected an was not translated. So then I found on forum library with FB for telegram 352. Then I have put FB in program, made instance DB for all devices (now I am using 3 inverters, but sometimes I use more then 10), same as before, put addresses in FB, HW config. is the same, but only one drive is working. Only thing what is different when I open FB with working inverter, and for others is the same, see pictures. So what I have to do to make it work? AttachmentPIC1.pdf (334 Downloads) |
6/6/2017 8:39 AM | |
Posts: 7 Rating: (0) |
Here is the picture with values, for not working inverters.
AttachmentPic2.pdf (270 Downloads) |
6/6/2017 4:26 PM | |
Joined: 10/11/2006 Last visit: 10/18/2024 Posts: 5925 Rating: (810) |
Hello Kruska, In order to to address more than one inverter, each inverter has to be called by the FB10 with its own IO Adress from the HW config. In- and out address have to be identical! Example and documentation: https://support.industry.siemens.com/cs/de/en/view/60441457 |
With best regards, |
|
6/6/2017 6:13 PM | |
Posts: 7 Rating: (0) |
Thanks guys, i didn't know about HW ID, now all works. Best regards, Kruska |