4/15/2008 7:35 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating:
|
Hello Patty; Unfortunately, SFC12 and FB125 work indipendantly, and FB125 picks up the missing slaves (even disabled) and shows them as in erroron the screens it is connected to. The suggestion on this FAQ is to use SFC51 (there is a mistake in the document) to read the status of enabled slaves on the master interface. http://support.automation.siemens.com/WW/view/en/19913996 Once you have this info you might use it to block the indication of missing slaves in your screens? Hope this helps, Daniel Chartier |
4/15/2008 7:55 PM | |
Joined: 2/27/2008 Last visit: 1/5/2022 Posts: 11 Rating:
|
I figured that was the case, thanks for the info. |