Hello, I’m starting to learn how to program a PLC (ladder), as such my knowledge is greatly limited/reduced. So I will appreciate all the help possible. I’m doing a project where I trigger a micro pump and I would like to measure the flow. I’m using a CPU 1214C (DC/DC/DC), an SM 1231 (8AI – 13bit) to receive the signal and a KTP700 panel 7’’ to show the value. To measure the flow rate I’m using an Omega component (FTB2003), which has the following characteristics (http://www.omega.com/manuals/manualpdf/M3236.pdf): - - The output signal is a square wave signal, whose frequency varies linearly with flow rate;
The pump part I can do, however I do not know how to handle the flow sensor signal. How can I do this? Is there some block that I can use?
Can you help me please? Thanks in advance,
Bruno |
|||||||||||||||
5/28/2015 8:59 PM | ||||||||||||||||
Joined: 7/7/2010 Last visit: 11/6/2024 Posts: 15385 Rating: (2443)
|
If you wire the pulse train input as a HSC input, set it to frequency and adjust the integration time values in the hardware configuration to suit. The result will be an analog signal representing 0 to 100% flow in pulses per second. You will likely want to normalize and scale this input signal to generate the various user units you need. For example, to scale from 0-100%, If I read the specs correctly, NORM function with input range in 0-1150. The output will be floating point from 0.0 to 1.0. Take the normalized output and feed to a SCALE block. The min max parameters for the SCALE block will convert the NORM block's output to user units. Put in 0 for min, and max range value for whatever units are available. The sensor is not guaranteed to be linear below a certain value. If you perform a calibration at those lower levels, you can override the norm/scale results and use a look-up table for the low end flow values rather than indicating they are out of range on the HMI.
|
|||||||||||||||
science guy |
||||||||||||||||
Follow us on