5/25/2019 11:47 AM | |
Joined: 6/15/2016 Last visit: 11/7/2024 Posts: 150 Rating: (2) |
good noon. without stop PLC hardware configuration download is possible or not? |
Regards, |
|
7/8/2019 5:58 AM | |
Joined: 4/28/2015 Last visit: 11/17/2024 Posts: 100 Rating: (4) |
not possible |
Kalleh dairy Co. |
|
8/26/2019 10:40 AM | |
Posts: 15 Rating: (0) |
Hi, Plc Hardware configuration is not possible during run time beacause S7-300 PLCs do not support changing configuration in RUN mode. To download modifications of Hardware the CPU must go in STOP mode. You can read more in software redundancy manual. With regards, Huzi.saify |