1/6/2019 1:17 AM | |
Joined: 6/23/2008 Last visit: 7/11/2024 Posts: 1167 Rating:
|
Hello grifasp, You should consider the Software SIMATIC PDM for your PCS7 Engineering Station. See information given here. Simatic PDM comes wit a huge device library (EDD) not only for Siemens devices. More information about the device library (including a link for download of the device library) can be found here. If a device is not included in that library you should contact the manaufacturer of the device and ask for an EDD for this device. To be able to route from the Engenineering Station down to the devices your devices need to be connected by means of HART communication capable I/O-Cards to the controller. Please consider the document "SIMATIC Process Control System PCS 7 Released modules" from this link to check the suitable I/O cards. Make sure you select your PCS7 version in the combobox before downloading the document. Best regards... |
"Expert" does not necessarily mean Siemens employee. Please cross-check your requirements always with official Siemens documentation. Also "Experts" are pleased about feedback. Please don't send support requests as PM. Questioners who don't follow up their thread will be put to my list of users to be ignored. |
|
This contribution was helpful to
2 thankful Users |
Follow us on