8/16/2016 9:13 PM | |
Posts: 15 Rating:
|
i want help to install gsd file to make profibus between s7 200 and s7300 but i want gsd fهiles to install it in simatic hardware catalog |
8/16/2016 9:44 PM | |
Joined: 9/27/2006 Last visit: 7/16/2024 Posts: 12268 Rating:
|
Hello asd; In the following FAQ, you will find a link to the gsd file for the EM 277, a link to the procedure to insert it in the Profibus master's configuratr files, and a step-by-step guide to configuring a S7-200 CPU (with an attachd EM 277) as a Profibus slave to a S7 master. How can you communicate data between the S7-200 and the S7-300 via PROFIBUS DP? https://support.industry.siemens.com/cs/fr/en/view/2615830 You should open your Profibus slave lists in the Profibus confiurator, normally the EM 277 is already included, if the master is a Siemens PLC. If it is not, use the attached gsd file, taken from the link above. Hope this helps, Daniel Chartier Attachmentem277.zip (1474 Downloads) |
This contribution was helpful to
3 thankful Users |
8/16/2016 10:01 PM | |
Posts: 15 Rating:
|
thank you very very much |
2/26/2019 10:34 PM | |
Posts: 1 Rating:
|
thanks |