10/26/2010 3:59 PM | |
Joined: 9/27/2006 Last visit: 7/14/2024 Posts: 12268 Rating:
|
Hello ROCLIM; If this is not clear enough, you will have to contact the manufacturer or reseller and ask them more details on this slave. |
This contribution was helpful to
1 thankful Users |
10/27/2010 2:25 PM | |
Joined: 1/28/2009 Last visit: 7/11/2024 Posts: 6844 Rating:
|
Hi ROCLIMBefore starting cyclic data transfer between DP master andDP slave, DP master transfers some sort of parameter data and configuration to the DP slave. Default parameters is definedby the GSD file and some can be change by user interface which isprovided in H.W config editor. The structure of these parameters defined by EN 50170 and the most known are -operation with watchdog -ability to be clustered into groups for sync and freeze -user_prm_data which is the hex parameter you mentioned in yourQuestion. This determines application-related data for the DP slave suchAs default setting or controller parameters. The default value is embeddedin GSD file by name of Ext_user_prm_data_const(0) .
Attachmenttest.bmp.zip (269 Downloads) |
Last edited by: hdhosseini at: 10/27/2010 2:55 PM |
|