11/6/2023 4:33 AM | |
Joined: 11/24/2017 Last visit: 11/4/2024 Posts: 5 Rating: (0) |
Hi everyone, I had a problem during I tried HMI and laptop connection, it always showed "the selected online target could not be reached". I have set the PG/PC interface IP to S7online, Static IP address... even though I " go online" both PLC and HMI, it still worked properly as my enclosed file. Could you give me some advice for this situation? Thanks very much AttachmentStep checking HMI fail connection.pdf (238 Downloads) |
11/6/2023 6:13 AM | |
Joined: 1/21/2013 Last visit: 11/12/2024 Posts: 3262 Rating: (507)
|
Hi binh77, Have you tried to start the transfer mode manually on your KTP1200 Basic? Please refer to chapter 6.4 of the "Basic Panels 2nd Generation" operating Instructions for details. You can also check if the automatic transfer mode is enabled, see chapter 5.18. Kind regards |
11/6/2023 7:26 AM | |
Joined: 11/24/2017 Last visit: 11/4/2024 Posts: 5 Rating: (0) |
Thanks Stefan, Unfortunately s.o set "start immediately delay time 0 seconds", so I couldn't choose transfer mode in start-up HMI. Could you know how can solve it?
|
11/6/2023 7:54 AM | |
Joined: 1/21/2013 Last visit: 11/12/2024 Posts: 3262 Rating: (507)
|
Hi binh77, If the HMI project starts automatically without delay and the project does not have a button to stop the runtime, open the control panel, etc., you need to reset your device to factory defaults. This is described in chapter 6.8 of the operating instructions and the necessary recovery software can be downloaded here. Kind regards |
11/6/2023 2:48 PM | |
Joined: 11/24/2017 Last visit: 11/4/2024 Posts: 5 Rating: (0) |
Hi Stefan, I updated to Tia V15, the problem is solved right now. thanks very much.
|