Hi, this is my first post here and I wannt to say Hallo. I have problem with making to work dunction keys of HMI Device KP300 with LOGO 12/24RCE 0BA7 over ethernet. I succesfull make to see B012 Counter on KP300 but when i try use function key (F1) nothing happend i connect in Logo!soft comfort F1 - Logo! TD Function key to reset input of B012 conter but , this isn't working. KP300 is configured in TIA Portal, comunnication Logo 0BA7 <---> KP300 working fine. I can change value of conter ofer cursor and delete key on KP300 screen but i need to use function (F1) or else. THX EDIT1 I have progress. I create button on screen and use hotkey with function key and this work. Is posibble to use Function key directly? Is posiblle to turn off possibility to change value of counter by cursors and esc key od TD?
Attachmentgotowe.zip (351 Downloads) |
Last edited by: Kashue at: 1/22/2013 2:15 PM |
|
1/22/2013 2:18 PM | |
Posts: 2930 Rating: (432)
|
Hi, the LOGO! TD funktion key F1 to F4 are not the functions keys of a KP300. Thes only relates to the function keys of the LOGO! TD. Hope this helps |