Joined: 4/28/2015 Last visit: 11/20/2023 Posts: 34 Rating: (0) |
Thank for your answer. One more question that how to communication btw touch screen? because there is IP address communication. but 400H has different IP address... ------------------------------------------------------------------------------------------ |
Last edited by: aisan at: 12/10/2020 04:39:50Last edited by: Jen_Moderator at: 12/15/2020 12:18:19New subject after splitting |
|
12/10/2020 3:59 PM | |
Joined: 9/27/2006 Last visit: 11/4/2024 Posts: 12293 Rating: (2690) |
Hello aisan; Do you mean your HMI IP address is on a different subnet than your H-CPUs? Have a look at this document then: Is cross-subnet communication over Profinet possible? https://support.industry.siemens.com/cs/my/en/view/109479139 You will find different suggestions to connect your HMI, such as a router, a PN-PN coupler... You will have to design a MRP connection adequately when adding such equipment (it might be easuer to simply chage the subnet of the HMI) Hope this helps, |
Last edited by: dchartier at: 12/10/2020 16:07:39 |
|
12/10/2020 9:20 PM | |
Joined: 9/27/2006 Last visit: 11/4/2024 Posts: 12293 Rating: (2690) |
Hello aisan; Establishing a connection between an HMI panel (Siemens) t with a S7-400H redundant system is discussed in this document: Connecting SIMATIC HMI panels with a SIMATIC S7-400H (WinCC V16 and STEP 7 V5.6) https://support.industry.siemens.com/cs/ww/en/view/96837136 Note that the proposed solutions will depend on the type (family) of HMI you are planning to use. Hope this helps, Daniel Chartier |