6/5/2008 9:40 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating:
|
Dear Vahid, In the handbook you might find all information to check the configuration. Manual ET 200S Motor starters (incl. Safety integrated system) |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|
6/6/2008 8:41 AM | |
Posts: 13 Rating:
|
Dear Late, Thank you for your reply and highly valued support. I have attached the result of the DB82, but I do not know how to use this DB and finding out the reason of the failure. As stated in page 113/402 ET200S manual each fault is indicated by a number but how can I find these figures?
The other problem is when we want to hot swap a faulty Et200S starter with a new one, If we stop the starter then the system is stopped, for example there are two cooling water pumps for each air compressor package with two individual starters ( slots 9 & 10) one pump is duty and the other is standby, if we want to turn off one of these starters then the whole of the system will be stopped, Could you help me to resolve this matter and having the capability of putting one cooling water pump in service and turning off the other starter and doing maintenance activity on the other cooling water pump. Do I need to make any changes in application program? AttachmentDB82.pdf (249 Downloads) |
6/6/2008 6:53 PM | |
Posts: 13 Rating:
|
Thank you for your kind co-operation. I am looking forward to hearing from you. Thanks in advance, vahid |
Follow us on