Hi, there are several failsafe-AO modules for ET200s. Have you had a look in the manual "S7 F - Safety Engineering in SIMATIC S7"? |
5/16/2011 10:51 AM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (308) |
Dear hari123 , I'm afraid it's not possible to configure AQ SIL2. This is conceptually wrong. A SIL2 is a grade for an SIS (Safety Instrumented System) which is required to driveyour plant to a safe state and consequently it doesn't require any analog outputs. So, the analog outputs are used only in process control which doesn't require a SIL grade. If you need this analog output for process control then you can use standard analog output module and configure it normally in the CPU that contains the F-Program and still your SIS system is SIL2 but only one CPU is used for SIS and PCS. Frankly speaking, some vendors other than Siemens do have SIL2 analog output modules for a very tight purpose called partial stroke testing. So, every know and then the module changes the position of the valve very slightly to make sure that valve is responding well. But still the final element (valve) has only 2 states, open or close not regulating. Best regards. H-H |