Hello, your existing TP177A project is created with which version of WinCC flex? |
11/17/2009 1:42 PM | |
Posts: 9 Rating: (0) |
I do not remember already, likely WinCC flex 2005 |
11/18/2009 11:55 AM | |
Posts: 26 Rating: (4) |
Hello, As far as I know you can only migrate from WinCC flexible 2008 to the TIA Portal V10.5 Regards, glubb |
This contribution was helpful to1 thankful Users |
11/19/2009 5:02 PM | |
Joined: 10/1/2008 Last visit: 2/5/2024 Posts: 21 Rating: (7) |
The problem you are having is because the 4" and 6" Basic Panels were not supported in the WinCC Flex 2008 version. You need to pick a different size panel or install a supplement file. Here are the steps you have to follow: 1. You must change the device in your WinCC Flex 2008 SP1 project to a Basic panel that was supported by WinCC Flex 2008. The 4" and 6" panels were not supported. If you want to use one of these panels then you have to install the Supplement_HSP_B4and6 add-on to WinCC Flex 2008 SP1. Unzip this file, close WinCC Flex 2008 SP1, stop the HmiES.exe process (or reboot the PC), and then run ApplySupplement.2008.cmd 2. Do a complete Generate (compile) of the WinCC Flex 2008 SP1 project 3. Using the Save As Version function select 2008. 4. Open Step 7 Basic 10.5 without opening any project 5. Select the Migrate project button and browse for the project you just saved then select Migrate. AttachmentSupplement_HSP_B4and6 (SaveAsVersion).zip (762 Downloads) |
This contribution was helpful to2 thankful Users |