2/25/2012 12:28 PM | |
Joined: 1/28/2009 Last visit: 12/5/2024 Posts: 6856 Rating: (1365) |
Dear metwally mustafa, Check the following link and thesample codes: With STEP 7, how can you control servovalves, frequency converters or current converters via a ramp-function generator? Also check the following solution,It was developed by SCL and I hope it helps you: [code]FUNCTION_BLOCK FB67 Best regards, |
Last edited by: hdhosseini at: 2/25/2012 12:37 PMLast edited by: hdhosseini at: 2/25/2012 12:29 PM//Project added |
|
This contribution was helpful to1 thankful Users |
2/26/2012 10:00 AM | |
Joined: 10/10/2010 Last visit: 12/5/2024 Posts: 307 Rating: (15) |
thank you my friend i will try the rate limiter program can i use the rate limiter for a PID controller (FB41)
|
3/4/2012 8:03 AM | |
Posts: 32 Rating: (0) |
Hi hdhosseini, Good day! May I also use this in my application? I will also put this in a setpoint branch. Also, I have something to clarify regarding the FIRST IN_OUT variable. Should the input connected to the its leg must be always on to enable and start the limiter or just a pulse? I am a little confused with the lines :
Thank you. Will be waiting for your reply. |
3/4/2012 2:59 PM | |
Joined: 1/28/2009 Last visit: 12/5/2024 Posts: 6856 Rating: (1365)
|
Thank you. Will be waiting for your reply. Dear ry_fern, Yes try it in setpoint branch to avoid step changes into your system. About "first" parameter, a pulse is OK but constant writing "TRUE" to that parameter should be avoided as algorithm internally manipulates (writes) values to that.Same issue discussed here: Why writing permanent values on MAN_ON,MAN parameters of FB58 is not recommendedBest regards, Hamid Hosseini |