6/15/2018 10:26 AM | |
Joined: 12/10/2015 Last visit: 12/17/2024 Posts: 10 Rating: (1) |
How to set tare? I used to set the tare value in s_IO_DATA TARE_VALUE in the WP231PE DB Now I have upgraded project to TIA 15. Suddently TARE_VALUE is read-only. How do I set the tare weight. If the current weight is to be used as tare, cmd 1011 will do, but I want to input a specifik value. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 6/18/2018 8:08:07 AMNew subject after splitting |
|
6/18/2018 4:08 PM | |
Joined: 1/4/2007 Last visit: 12/17/2024 Posts: 1166 Rating: (175)
|
Hello AutoGen, I also ugraded my TIA project to TIA V15. But I can set a new tare weight in my datablock! Also the command 1016 works . Attached you can find my TIA V15 project. Best regards Siwarexi AttachmentCPU1214_WP231PE_TP700_V110_TIAV_V15.zip (459 Downloads) |