Joined: 5/20/2015 Last visit: 9/2/2024 Posts: 216 Rating: (3) |
hello guys, i have ET200s with IM 151-8 PN/DP cpu which i want to communicate with simatic comfort hmi TO700,. i have configure alarm window with system and diag events, when runtime starts it show station is connected but tags wont communicate or update in hmi. you can see in capture pic of hmi during operation. red and green circles with simple appearence change animation. it means PLC is communication with HMI but tags not updating . what could be the issue/problem in my tag making configuration. attached screen shot please help. ASAP ------------------------------------------------------------------------------------------ Attachmentscreenshots.zip (47 Downloads) |
Last edited by: The Helping Hand at: 9/5/2017 9:28:35 AMNew subject after splitting Let's do it... |
|
9/4/2017 12:11 PM | |
Joined: 8/3/2009 Last visit: 9/18/2024 Posts: 13723 Rating: (1728) |
Hello gabbar It looks that you have configured a manual HMI Connection. you should use an integraded connection to be sure that everything works. Use a PLC Proxy : https://support.industry.siemens.com/cs/de/en/view/73502293 And then: https://support.industry.siemens.com/cs/de/en/view/89852595 And Please try to use a DB and a integer Tag for testing, if this works then you have to work on your adressing! Bye Murof |
Last edited by: Murof at: 9/4/2017 12:12:55 PMLast edited by: Murof at: 9/4/2017 12:13:22 PMIf this Information really helps, you could use the Rate function |
|