11/25/2018 9:56 AM | |
Joined: 1/26/2014 Last visit: 8/9/2024 Posts: 164 Rating:
|
Dear all, i added FM350-1 in my existing hardware.I have Cpu 416-3 and module added with ET200 (IM-153-2) but when i added i got some problem..FM module on fault and Main CPU 416-3 also on External Fault (EXTF). i think error related to CiR setting. can anyone felp me. I attached CPU Diagnostic buffer and also screenshot of CiR setting for CPU and for ET200M AttachmentDiagnostic.zip (56 Downloads) |
11/25/2018 10:10 AM | |
Joined: 9/9/2015 Last visit: 8/5/2024 Posts: 727 Rating:
|
Dear Jabbi_king, It seem like you have quite a number of errors inside. I suspect, 1. You did not set your Process Image Partition. Did you assign PIP for your I/O Address? What OB are you using on your IO address and what PIP did you set for them? 2. Slave 13, did you assign the counter module correctly? 3. CIR, did you assign it correctly? CPU external error is transferred from individual interface modules, and the modules error is transferred from individual IO/counter modules. You could delete the configuration one by one, check the diagnostic buffer and make sure the error is gone, then only you configure the next. This can make the troubleshooting easier. Hope it helps. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
11/26/2018 1:47 PM | |
Joined: 9/9/2015 Last visit: 8/5/2024 Posts: 727 Rating:
|
Dear jabbi_king, For the PIP, you may download the engineering manual to understand more. *Search for keyword like Process image partition, PIP, CIR I also attached the PIP screenshots in the attachment. For the FM350-1, you may refer to the manuals below. Simatic FM350-1 - Siemens Manual Simatic FM350-1 -Commissioning Hope it helps. AttachmentPIP.zip (58 Downloads) |
Last edited by: Jen_Moderator at: 11/27/2018 10:37:47 AMOptimized links. Please give me 5 stars Rating if my post is helpful for you. :) |
|