2/5/2010 3:35 PM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hello, Could you attach here copy of this project? Perhaps this link is helpful: Retentivity behavior of S7-300 CPU 31x best regards, Hristo Miahlev |
2/8/2010 3:26 AM | |
Posts: 71 Rating: (0) |
Hi there, Here is the attachment of the program. Thanks for the help.. regards createstars Attachmenttest.zip (284 Downloads) |
2/8/2010 4:44 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054)
|
Hello createstars Your 315-2 DP(6ES7 315-2AF03-0AB0 according to your HWconfig) is quite old and does not support usage of SFC82,83 and/or 84 as far as I can tell (you need a CPU with MMC to use this SFC's). To be sure, have a look online in the "Performance Data" and check if the SFC's exist in it (PLC menu-->Diagnostic/Setting-->Module Information-->Performance Data tab). Gut feeling tells me they do NOT exist which explains your problem with the download (the CPU rejectsthe download of FC1 because you are calling a SFC from it that doesn't exist in the opertaing system of your CPU). Please let us know what you find and you may also find the following link useful: What points do you need to remember during the handling of micro memory cards? I hope this helps |