10/3/2010 2:16 PM | |
Joined: 1/20/2008 Last visit: 9/18/2023 Posts: 120 Rating:
|
Dear Friends other questions are splitted to I think current on the I/O bus is provided by current consumption at 24VDC. Is it true or false?. AttachmentIM 153-2 Interface Module.pdf (167 Downloads) |
Last edited by: O_Moderator at: 10/4/2010 1:25 PMnew subject after splitting |
|
10/3/2010 3:20 PM | |
Joined: 7/2/2008 Last visit: 9/14/2023 Posts: 928 Rating:
|
Hello MRG, [schnippschnapp] It's 0.6 A. The 1.5 A is not there to deceive you but you should always make sure that the total consumption of your I/O & FM modules altogether doesn't exceed the 1.5A. For example,this FM particularly consumes 160mA from backplane bus which means you can never have 12 FMs at the right of an IM153-2. Best regards. H-H |
Last edited by: O_Moderator at: 10/4/2010 1:33 PMLast edited by: H-H at: 10/3/2010 3:21 PM |
|
This contribution was helpful to
1 thankful Users |