11/29/2017 9:21 AM | |
Posts: 28 Rating:
|
It's possible to update PID Compact parameters on HMI? If it's possible, how? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/29/2017 2:30:42 PMNew subject after splitting |
|
11/29/2017 2:40 PM | |
Posts: 28 Rating:
|
I want to change Gain, Td and Ti and update to PID with HMI. |
11/29/2017 2:51 PM | |
Joined: 7/9/2015 Last visit: 7/26/2024 Posts: 3897 Rating:
|
Hi, please have a look into the manual. SIMATIC S7-1200, S7-1500 PID controlThere you will find information like on PDF page 73: "You can only configure the setpoint, process value and output value in the Inspector window Instance DB: Regards, Towome |
|
|
11/29/2017 11:18 PM | |
Posts: 28 Rating:
|
If i understood correctly, i can't update parameters (Gain, Td and Ti) on HMI? |
12/7/2017 11:06 AM | |
Posts: 28 Rating:
|
It's that fine if i want to change PID COmpact parameter with HMI? (See the picture) |
This contribution was helpful to
1 thankful Users |