Hi Tomy, I thinkSitrans LG200/7ML1303- 2xxx: is the rightradar foryour measurement. There are several optionsthatIcan choosefrom PIA-selector to fix with the application. Assample image below |
[IMG]http://i17.tinypic.com/66b7jas.jpg[/IMG] |
|
8/12/2010 5:36 AM | |
Joined: 3/28/2010 Last visit: 11/8/2024 Posts: 1074 Rating: (214) |
1) Temperature If the top of the silo is 200°C or below, then an LR460 might work. 2) Material's dielectric constant 3) Use during filling If the filling flow stream interrupts a radar's beam path, then the energy is either absorbed or deflected elsewhere, either attenuating a normal signal return or producing false echoes. Some attention has to be paid to where the filling flow stream is in relation to where a radar might mount and how the material filling stream is likely to intersect. 5) mounting location: 6) Power 7) application data sheet |