Joined: 3/30/2020 Last visit: 8/14/2024 Posts: 4695 Rating: (974) |
Hello. The 'system time' is the setting for GMT+0. The 'local time' is the the one with GMT+5:30 applied. Use the online tools to set the PLC to the correct system time. Set in the hardware configuration the time zone and day-light-saving rule (by choosing a city name). For implementing user adjustable time settings, consider the 'LGF_SetTime' building block in the Siemens library: Library of general functions (LGF) for SIMATIC STEP 7 (TIA Portal) and SIMATIC S7-1200 / S7-1500 ~ |