1/10/2010 12:19 PM | |
Posts: 5 Rating: (0) |
Hello, I'm trying to use the SMS blocks described in (MAS 5), but i keep getting an error saying that i can't use (BGN_ITIME) and (CAL_ITIME) blocks since they are not supported by the CPU. I'm using CPU 222 REL 01.22. According this link, those two blocks are available for S7-200 CPUs from version V2. Is there a way to upgrade my CPU or make it support those blocks. Please note that the (BGN_ITIME) and (CAL_ITIME) blocks are essintial for the SMS blocks to work. Your help and support are highly appreciated. Regards, |
Last edited by: O_Moderator at: 4/14/2010 12:39 PMsubject edited |
|
1/11/2010 12:52 PM | |
Joined: 5/28/2008 Last visit: 7/15/2024 Posts: 1343 Rating: (141) |
Hi, PLC with REL 01.22 don't support BGN_ITIME and CAL_ITIME. Please take TON-Timer as Darius wrote. regards |