5/23/2012 3:18 PM | |
Joined: 7/8/2009 Last visit: 7/26/2023 Posts: 1974 Rating: (477)
|
F002 means Over Voltage Normally it is either due to high incoming voltage, or its because of regenerative mode If your supply is OK, then you have to try by increasing ramp up/down and if this is not working, you have to install breaking resistor Check this thread Regards Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
This contribution was helpful to1 thankful Users |
5/30/2012 2:15 PM | |
Joined: 6/4/2008 Last visit: 6/26/2024 Posts: 1485 Rating: (322)
|
Hi, The MLFB for the braking resistor as per the DA51.2 catalogue is found on page 75 (or section 4/17) The very simple connection of the braking resistor can be found on the block diagram on page 74 of the MM440 Operating Instructions Regards, Graeme |
6/5/2012 9:16 AM | |
Posts: 77 Rating: (1) |
Dear sir, only braking resistor is enough, they need any other accesserois for connections, for above given link am not find what i need braking resistor and also i confused how to set resistor for external connection. can you give me clear view for that, please help me sir, becoze i am fresher of this world
|