Joined: 6/14/2015 Last visit: 9/3/2024 Posts: 242 Rating: (2) |
Hello every body. I want to monitor PQWs, but it's not possible. what should I do? |
6/3/2023 2:28 PM | |
Joined: 9/27/2006 Last visit: 9/22/2024 Posts: 12282 Rating: (2685)
|
Hello akhbar_torkashwand; Step 7 v5.x has a quirk about peripheral addressing: you cannot use a VAT table to write to PIW, and you can't monitor a PQW directly. You can read a PIW and write to a PQW. The workaround for a PQW is to add a program line in whic you move the PQW value to a MW regster, for example), and monitor that value. See this discussion (among others): https://support.industry.siemens.com/forum/ca/en/posts/pqw-shown-cross/151333 Hope this helps, Daniel Chartier |