I have attached instructions for NCK and PLC general reset on NCU 7X0. From your discription it seems that you have executed general reset of NCK/PLC. On proper completion of general reset, the number "6" and a flashing dot is output on the status display of the NCU. So it cant be evidence of improperly execution of general reset. Contrary, different communication alarms occur during general reset, these alarms have no influence on how to continue. AttachmentReset NC and PLC.pdf (254 Downloads) |