Hello Dilli not too sure which manual you are using, but Status W#16#0830 (Event Class8, Event number 30hex) is described in the Modbus Master Diagnostic section on page211 of THIS manual and means that: "The response monitoring time has elapsed without the startof a response frame being detected" (andthe attachedpiccontains the possibleremedies/checks for it). I hope this helps |