P651 Can you explain where you get your information from?Can you explain where you get your information from? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/28/2023 10:30:46New subject after splitting |
|
6/29/2023 11:20 AM | |
Joined: 6/4/2008 Last visit: 10/4/2024 Posts: 1497 Rating: (324)
|
Hi, we look in the compendiums (manuals) See below, simply choose the type and firmware version of the control unit you have and then navigate to either the Function diagrams or the actual parameter list. i.e. if your firmware version is V1.66 or below, then choose the V1,66 version else, choose the higher V2.5 version. Alternatively, you can select P651 in Drivemonitor and press the F1 key to see the explanation of the parameter. SIMOVERT MASTERDRIVES Vector Control Compendium VC34 (Operating Instructions) Compendium Motion Control (MC 1.66) SIMOVERT MASTERDRIVES, MOTION CONTROL, COMPENDIUM (MC 2.5) P651 from Manual S.DigOut1 BICO parameter for selecting the binector whose value is to be output at terminal -X101/3 of the terminal strip for the basic unit. In order to use terminal -X101/3 as a digital input, both indices must be set to 0. i ndex1: 107 Unit: - Indices: 2 ,BDS Type: L2 ,B Menus: - Parameter menu + Terminals - Upread/free access Changeable in: - Ready to switching on - Operation enabled