Hello Bibounours; You seem to think that your OPs are Profibus slaves. They are not, they are Profibus masters (class 2) and they cannot be configured as part of the PLC's Profibus network, You set the communication parameters in each OP using Protool or WinCC Flexible software, and if you want to have direct access to the PLC's tags, then simplyintegrate the project in Step 7: Advantages of Configuring with ProTool integrated in STEP 7 How do you integrate a WinCC flexible project in STEP 7? Hope this helps, Daniel Chartier
|