11/11/2010 12:45 PM | |
Joined: 3/21/2006 Last visit: 12/2/2024 Posts: 10229 Rating: (1181) |
More details at Data Communication via Modbus/TCP with S7-1200 (CE-X22) BR, Hristo Mihalev |
11/15/2010 8:50 AM | |
Joined: 10/7/2005 Last visit: 12/20/2024 Posts: 3029 Rating: (1058) |
The 1200should indeed be able to communicate with up to 8 PAC3200's at the same time as per technical spec of the 1200 manual and THIS FAQ (Modbus on TCP will use the T-Blocks related TCP connection even though the Example does not seem to explicitly state this). |
Cheers |
|
This contribution was helpful to1 thankful Users |
11/15/2010 2:09 PM | |
Joined: 7/7/2010 Last visit: 12/20/2024 Posts: 15527 Rating: (2461) |
Thanks! I am very glad to know this. |
science guy |
|
This contribution was helpful to1 thankful Users |