Dear Expert, I am having S7 400f/fh with IM where i have configuration like IM accompnied by Fail safe modules and lastly the standard AO module so after refering the above posts i understand that i will nopt require 6ES7195-7KF00-0XA0 safety protector in between the fail safe and standard modules correct me if i am wrong and if right, i request for the official document for this type of safety system and its urgentSmit Shah------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 12/2/2015 2:00:40 PMNew subject after splitting Thanks and Regards |
|
12/2/2015 3:20 PM | |
Joined: 5/28/2008 Last visit: 9/9/2024 Posts: 4515 Rating: (839) |
Hello, In Old systems with old Fail safe modules, Safety Protector was necessary to achieve SIL3/Cat4. But Now, It's clearly mentioned in the data sheet of ET-200M Fail Safe modules the following statement: data sheet of ET-200M Fail Safe modules Please see them in the following manual: SIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modules |