1/19/2009 2:57 PM | |
Posts: 1776 Rating:
|
Hi, have you seen this FAQ http://support.automation.siemens.com/WW/view/en/24325381 |
1/21/2009 1:53 PM | |
Posts: 31 Rating:
|
Hi again Jaapie! Thanks!! I am using v7.0. Next week will be fine bugmenot |
1/21/2009 10:03 PM | |
Joined: 1/17/2006 Last visit: 5/20/2025 Posts: 800 Rating:
|
Hi bugmenot, I have created a PCS7 V7SP1 WinCC project for you, but you can open it with you version 7. The only thing is that I can not post it here. It is to big. So post only the two things you need. 1-The global script (put it in WinCCProjectName\Library) open global script and compile all headers and open the script and compile it. It should show 0-errors. 2-The Testpicture with two buttons and an alarm ocx on it. In alarmlogging you have to configure like earlier discribed (with the @1%s@...in the textblocks) the 1 in this @1%s@ is the first text you will fill in. You must configure messaline 1 (can be changed within the script) So now you have everything to create operator messages. If you need the project I can send it a different way, let me know.... Good luck, Jaap AttachmentShare.zip (983 Downloads) |
Last edited by: Jaapie at: 1/21/2009 10:06 PM |
|
This contribution was helpful to
1 thankful Users |
Follow us on