5/21/2007 5:24 AM | |
Posts: 11 Rating: (0) |
Thanks Late! I will consider changing to Scalance X200. |
5/22/2007 3:37 PM | |
Joined: 9/28/2005 Last visit: 10/24/2024 Posts: 414 Rating: (28) |
Hi, Have youthought abouta second ethernet connection/network for a redundant connection to your S7-400H-system? Then you also need a second CP1613A2 in your PC and of course a CP443-1 card in the second part of your S7-400H-system. For more information on S7-Redconnect see also the attachment or IKPI-2007 page 2/219 and on. Attachments7-redconnect.pdf (752 Downloads) |
Smurf |
|
5/25/2007 12:45 AM | |||
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating: (318)
|
Hi, That is possible, when you have the newest Scalance X200 switches then there is a redundancy manager in the switch (only in the newest !!), with that switches you can make a ring where all equipment could be coupled to. {with the older ones you need a IRT-switch in the ring}. The difference to one or two CP 1613 A2 is that you could make two seperated rings where all the equipment is devided from each other. It is also possible to use them both on one network, but then you trust the PC more then the network and the CP-card. |
||
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|||