7/13/2016 5:53 AM | |
Posts: 12 Rating: (0) |
Hi experts i am using CPU 410 smart processor and software is PCS 7 V8.2. I have configured hardware configuration and it is download well ( hardware used is SIMATIC ET200PA with one input module and one output module) now i used to program in the OB block and created ladder program and when i downloaded it showing some error that is OB block is not copied that attached here.please find it and help me to download program to cpu 410 smart ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 7/13/2016 9:04:12 AMNew subject after splitting |
|
7/13/2016 7:40 AM | |
Joined: 3/14/2008 Last visit: 9/13/2024 Posts: 2095 Rating: (936)
|
Hi, At the screenshot, you have opened OB1. You have to close this before downloading. Otherwise, download cannot proceed. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
7/14/2016 6:23 AM | |
Posts: 12 Rating: (0) |
hardware configuration image |
Last edited by: Benil at: 7/14/2016 6:24:17 AM |
|
7/14/2016 6:25 AM | |
Posts: 12 Rating: (0) |
SIMAT ET 200PA image |
7/14/2016 6:26 AM | |
Posts: 12 Rating: (0) |
|
7/14/2016 8:14 AM | |
Joined: 3/14/2008 Last visit: 9/13/2024 Posts: 2095 Rating: (936)
|
Hello Benil, Normally, you would not want to adjust/create OB1 in any ways in PCS7. OB1 is created automatically in the "Blocks" folder and you cannot adjust it. Any blocks that you insert in CFC chart, which are called in OB1 are handled automatically in OB1. It seems that you do not have Simatic Manager setup as PCS7 project. I'm missing the "Charts" folder, which should be listed under "S7 Program (1)" under the "Blocks" folder. How did you create the project? Not by the PCS7 wizard I believe... Can you check this? Under the project name (work 6), right click->Object Properties and next to "Use" it should says: "PCS7". Furthermore, I recommend you to create a multiproject, where you will add individual projects. Basically, you the layout is this: Multiproject: ---------------AS1 project ---------------AS2 project ---------------OS project ---------------Client project ---------------Master library To see more info, see the following link with manuals of PCS7 v8.2 A good place to start is under the topic: "Getting Started". This manual (two parts) provides a step to step guide with an example project. Normally, when you want to add custom blocks/logic, you will use SCL to program the logic, which you then compile as block so it can be used in the CFC charts. In SCL you also could make logic that should be handled when OB1 is called. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
7/14/2016 2:24 PM | |
Joined: 3/14/2008 Last visit: 9/13/2024 Posts: 2095 Rating: (936)
|
Hi Benil, You don't have to add the CPU in the PCS7 wizard right away. You can create the multiproject and add your CPU later. But, you have to do one thing for me. Please open Hardware configuration and on your right you see the Hardware catalog. There should be a profile selected. The profile should be set to: "PCS7 V82". This will make sure that you can only select components which work with PCS7 v8.2. If your MLFB number is not listed, it means it is probably not released. The CPU410 SMART has 1 CPU that is released: 6ES7 410-5HN08-0AB0 with firmware v8.0/v8.1/v8.2. If you have another type, then this could be your problem after all... Thanks for the rating, glad to help! |
Last edited by: Oreca at: 7/14/2016 2:25:49 PMIf I could help you, you can use the RATE button. Thank you. |
|
8/18/2016 11:07 AM | |
Posts: 12 Rating: (0) |
Thanks orecka for your support .i got solve that problems ,problem is downloading..i was downloaded entire program ..only we have to download the chart itself |
Follow us on