9/7/2021 8:13 AM | |
Joined: 3/14/2008 Last visit: 5/14/2024 Posts: 2066 Rating: (928)
|
Hi Berg, The CPU410 has two licenses: AS RT PO which are the countable licenses and AS PO which need to be present on the CPU. The first license is needed for each PO like a Valve, Motor, SFC etc. In the overview you have configured 738 PO and 728 are booked. You have a total of 1300 AS RT PO available and but only 1 is still available. You are missing 10 PO for the download. The AS PO license is a license that scales the CPU410. The CPU410 has the best performance of all CPU's, but the AS PO licenses let's you scale it to your application thus paying only what your application need, using the best CPU. Your CPU410 has a limit of 1600 AS PO and currently 728 are booked to the CPU. If your limit is reached, you need to purchase additional AS PO and activate it via a SEC card. There is a procedure for this. But looking at your print screen, you need to buy additional AS RT PO.
|
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to2 thankful Users |
9/7/2021 2:22 PM | |
Joined: 1/11/2019 Last visit: 4/30/2024 Posts: 702 Rating: (140) |
Attachment 2 |
Follow us on