2/19/2015 5:58 AM | |
Posts: 4 Rating: (0) |
Hi, I am using PCS 7 V8.1 I am facing problem during OS compile. Also in OS configuration window , whenever i am trying to download configuration to PC-Station it shows "THE CONNECTION TO TARGET MODULE CANNOT BE ESTABLISHED". I have done all settings properly but not finding any solution over this issue. ------------- |
Last edited by: Min_Moderator at: 2/19/2015 10:03:07 AMNew subject after splitting |
|
2/19/2015 11:18 AM | |
Posts: 4 Rating: (0) |
Hi, I have stand alone system ES and OS , no Server-Client Configuration. For your reference i have attached snapshot here. AttachmentS7_connection.docx (364 Downloads) |
Last edited by: Min_Moderator at: 2/19/2015 11:28:24 AMDelete false quote |
|
2/19/2015 12:18 PM | |
Joined: 3/14/2008 Last visit: 9/8/2024 Posts: 2094 Rating: (936) |
You have to configure a plant wide connection. That means you need to set the PLC Ethernet card to a communication protocol (TCP/IP, ISO) and you need to configure the OS station card (IE general) the same. Then you need to merge the connections (Go to your multiproject, right click and select Multiproject->Adjust projects and select the subnet to be merged (Ethernet). Then a plant wide connection is made and you can compile your OS (please check if you need to save and compile the netpro data again for your cpu) |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |