HI Kristof74, important for the PN/PN coupler is, the other side can be outside of the project -but- another controller on X2 including a valid configuraiton on this side is mandatory! Just removing the other PLC and leaving X2 open does not work. So question is: Is X2 configured in another systen including a PROFINET controller and is his side also connected? SIMATIC Bus links PN/PN coupler