9/17/2020 12:18 PM | |
Joined: 3/14/2008 Last visit: 9/2/2024 Posts: 2094 Rating:
|
Hi, The CPU410 is scalable in performance. It means, you have the highest performance CPU, but you need to scale them to your application needs in the form of PO. Apart from that, you still need AS PO for each object. The AS PO is stored in your ALM. It's a bit confusing, but it comes down to: - AS PO for each PO object loaded to the CPU. These licenses are booked to the CPU and will be drained in ALM. - PO objects loaded to a SEC card inside the CPU which scale the CPU according to the application. What does this mean for you: At the moment, 800 AS PO are booked to AS1, your CFC program demands 800 AS PO. The PO limit of AS1 (which is a CPU410) is 800 as well. If you want to load 5 valves for example, 5 AS PO is booked to AS1 from ALM. The currently still available AS PO would be 8335-5=8330 AS PO. However, you need to upgrade the PO limit of AS1 to a minimum of 100 PO. You need to order this: 6ES7653-2CA00-0XE0 (100 PO). If you have upgraded, the PO limit is set to 900. The PO are available in 100 and 500 expansion packs. Please note the following: - If the AS is redundant (2xCPU410), you need to order 2x the same expansion pack. - You need to activate the expansion via a SR and load the activation file to the CPU. This will take some time. Please check the following link for more information and activating the PO:
|
Last edited by: Oreca at: 09/17/2020 12:28:03If I could help you, you can use the RATE button. Thank you. |
|