2/8/2015 8:19 AM | |
Posts: 4 Rating: (0) |
Hi. We checked our actuator by manometer during 24 hours, but air doesn't lose from actuator. Also we checked Sipart by manometer (picture "Check positioner" in attachment) - pressure decrease always. We checked manometer and fittings by soap water. We found leakage in enclosure ventilation by soap water (picture "Leakage.jpg" in attachment.). When positioner set actuator >0%, we see this air bubble. When position is 0.0 %, we have not this air bubble (when actuator have not air). Why does air lose through it? We didn't remove the inside container. We have 3 new Sipart PS2, and we have this problem with all. AttachmentSipart.zip (349 Downloads) |
10/4/2016 10:11 PM | |
Posts: 1 Rating: (0) |
Hello, I'm experiencing the same problem described before on two new valves equipped with sipart sp2. It seems that the controller does not block the air to keep the setpoint, it periodically vents some air, causing losing of position, then it moves again the actuator in order to follow the set point. This behaviour makes me crazy, is there any parameter to set in order to stop these oscillations? Just to underline: the oscillation occurs every 1-2 minutes depending on the valve position, moreover when the valve suddenly loses its position I can hear the opening of the piezo inside the Sipart. Finally, the leakege test says 0.0 and I have noted that if I go in the setting menu when the valve has reached the setpoint the sipart doesn't move the valve!! Here a video of the behaviour (fixed setpoint of 20%) Any idea? Regards |